Major violations:
1)Excessive spans on unsupported pipe (PVC must be supported every feet and within 1 foot of change in direction.
2)No metal hangers allowed on PVC pipe
3) Clean out required wherever there is a change in direction greater than 45 degrees.
4) Tee's are prohibited on horizontal lines.
5) max vertical drop from a drain to a trap is 24" also if one assumes that there are traps above the floor then all the traps in the photo are illegal because code prohibits double trapping. Also a couple of the traps are too deep...code says the water level must be between 4 and6 inches.