From a copy of the Florida building code which is verbatim from the national code. State or local codes can add to the requirements (like requiring metal pipes or exterior discharge).
I can't tell you how many re-inspections I've generated by missing or improperly installed discharge pipes as many of these retrofits are DIY. And not just FHA/USDA. If it is not installed on a conventional appraisal I will still photo and comment on it, and describe the dangers -- kids face gets scalded
-- and how cheap the fix is ($20). I add the plumbing code, and state there is no record of a permit for a professional install. I don't stip for it to be installed on conventional, but it puts the lender on notice, and documents a danger. About 80% of conventional underwriters who are usually national will require it to be installed.
504.6 Requirements for discharge piping
The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:
I can't tell you how many re-inspections I've generated by missing or improperly installed discharge pipes as many of these retrofits are DIY. And not just FHA/USDA. If it is not installed on a conventional appraisal I will still photo and comment on it, and describe the dangers -- kids face gets scalded

504.6 Requirements for discharge piping
The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:
- Not be directly connected to the drainage system.
- Discharge through an air gap located in the same room as the water heater.
- Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
- Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
- Discharge to the floor, to the pan serving the water heater or storage tank, to a waste receptor or to the outdoors.
- Discharge in a manner that does not cause personal injury or structural damage.
- Discharge to a termination point that is readily observable by the building occupants.
- Not be trapped.
- Be installed so as to flow by gravity.
- Terminate not more than 6 inches (152 mm) above and not less than two times the discharge pipe diameter above the floor or flood level rim of the waste receptor.
- Not have a threaded connection at the end of such piping.
- Not have valves or tee fittings.
- Be constructed of those materials listed in Section 605.4 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.